Scotty is correct, the OP stated that the motor includes a built-in VFD so the voltage/current ratings are probably at the VFD terminals, not the motor terminals. I note that both ratings equal about 28kVA which is probably about right for a 22kW motor/VFD combo.
I have employed a similar strategy for customers requiring multiple voltage/frequency ratimgs. The input voltage and frequency to the VFD are irrelevant, within limits, as long as the voltage is high enough to supply the motor. I suspect that the motor itself is rated for 380V/50hz and the internal VFD is hard coded to provide this voltage/frequency irrespective of the input voltage/frequency (within the 380V/50hz-480V/60hz envelope). If this is the case, the current at 415V will be about 40 amps.