Parchie -
You certainly have some excellent points. However, I don't think I am down playing the importance of motor overload protective functions.
When you say "most in the manufacturing industry see it as a "profit/loss" item", I'm curious as to exactly which industries. Cause, I don't see that much, especially for smaller motors - say under 200 hp.
Caution {rant-on} suggest burn before reading
I've been involved in Oil and Gas refinery and pipeline, petroleum bulk plants, pulp industry for around 50 years (welders helper, 1965). Engineering since 1973. The majority of my clients (not so much for bulk plants) are concerned with high reliability, running flat out, 24/7. They would insist on 365 days per year, if maintenance shutdowns weren't mandatory. Starting from that mindset, the concept of a dead fractional horse power motor showing up on the P/L statement is completely alien. Now consider that some processes are conceptually a series string of 50 pumps/motors with maybe as many valve actuators. One miserable 3/4hp motor can take down the whole process. Common practice is to have install spare pumps/motors for every critical piece, yep, right up to multi-thousand horsepower.
Considering this mindset, is it suprising that unless specials are involved, fractional horsepower may not be repaired at all, under 10hp may not be considered for rewind. Generally there is no squawking if a motor trips on OL. Things do break - manmade, it will break - that is a fact. However, generally, if the customer could remember the last time, they are telling me they want to investigate increasing the reliability.
Consider the customers are not whining about the motor costs, rather they are majorly whiny about the downtime to repair. Okay, you say, keep the overloads set down and they won't burn up and require replacement. Possibly. Maybe in the world of IEC motors, it is necessary to design for 90% loading and set the overloads at 100%. I couldn't tell you - no experience. Nema motors, the design will be as close to 100% loading as possible. Most clients will opt for 1.15sf to increase MTBF. And the OLs will be set 125% - 140%. And truely, I've never had a motor burn up (winding failure) because the overloads were set up to NEC max. They burn up because:
[ul]
[li]The windings shook a hole in the insulation;[/li]
[li]5 years of high ambient, heavy load, 24/7 finally took its toll. When one considers that is close to 50Khrs - that's not bad;[/li]
[li]Bearings failed and put the rotor into the stator;[/li]
[li]Cleanup crew using a fire hose (pulp mill - amazing how much water one can get past the shaft on a TEFC with a fire hose);[/li]
[li]Operators can adjust process to overload motor and trip. Reset repeatedly until the smoke comes out. (Pulp Mill - wood room) OLs with thermal model not commonly available.[/li]
[li]HVAC air handler designers spec/buy 1.0SF 208-230 motors, load them right to 100%, locate in high ambient areas, and then are suprised when they burn up frequently. Fortunately this one is easily fixed. Replace with 200V, 1.15sf motor - often same footprint, just twice the money. Yes, on 208V systems, heavily loaded 208-230V motors run hotter than 200V motors. Twice the money pales next to repair/replace every few years[/li]
[li]And one that maybe could have been saved by overloads. Definitely could have been saved by a modern electronic overload/motor protection relay. 4160V, 900hp, 900rpm to a hydraulic speed reducer, driving an ID fan. Fused contactor, no overloads, operator set the load by adjusting the speed reducer output RPM, relying on a winding RTD readout. One fuse opened, motor single-phased for maybe 30 seconds. Ruined it beyond rewindable. Don't know why the fuse opened. Electronic motor protection not commonly available - not uncommonly available either. We put in a phase loss relay. Don't know why they did not have one before.[/li]
[/ul]
So where am I headed:
[ul]
[li]Yes, saving the motor or limiting the damage to the motor is important.[/li]
[li]Putting out the fire is top of the list. Especially since there may not be a motor to save anyway.[/li]
[li]Fractional hp rarely (like never) make the list of financial concerns.[/li]
[li]Advising to set OL at 100% sounds wrong on so many levels.[/li]
[li]Yes, plenty of us can read.[/li]
[li]Automatic assumption that the OP had not bothered to correctly set the OL and that caused the original motor failure does not sit well.[/li]
[li]Up to a few hundred horsepower, replacing a motor is just a cost of doing business.[/li]
[li]The more expensive the motor, the more extensive the protection (Really? Well thank you Captain Obvious)[/li]
[li]I have not been around any industry where the cost of a fractional horsepower motor could ever possibly matter. The down time will, but not the motor.[/li]
[li]Yes, it is always about the money[/li]
[li]Example: Say you have an installation where a fractional/integral hp motor experiences 3 trips/ year resulting in 1 hour downtime and a plant startup each trip. One sets the overloads up to max and gets no trips for two years, then motor burns up. Takes 10 hours to replace motor, maybe a problem. Takes 1 hour to change a motor - not a problem.[/li]
[li]I highly suspect we live/work in different worlds - and that is okay. We all have to make a living. However, the rules for one likely do not fit the other[/li]
[li]Yes, it is always about the money.[/li]
[/ul]
if you got this far, thanks for listening {/rant-off}
continued overload philosophy per
the worm
Harmless flakes working together can unleash an avalanche of destruction