- Jan 16, 2003
- 15
First I will describe the setup. A 100 kva generator is operating a small ice plant. The voltage is 208 V/3 phase/60 Hz, Wye. The loads are as follows: 15 hp refrigeration compressor, 4 hp condenser fan, 1.5 hp pump, air conditioner (draws 24 amps) (all previously listed are 3 phase, 208V), (3) 1 hp single phase motors (augers, blower).
On 2 occasions, 2 different motors were locked up due to an ice blockage - one single phase motor operating an auger and one 3 phase motor operating a cutter assembly. The motor overloads did not trip (fuses in the case of the single phase motor and overload relay in the case of the 3 phase motor). Instead, the motors just started heating up in a locked condition. Luckily, I was able to find that the motors were stalled and I shut off power before the motors burned up. In the process of troubleshooting why the motor was not running, I checked the voltage. It was "pulled down" to 165 volts.
My theory on this is that there is not enough power in the supply to maintain the voltage to a sufficient level to allow the motor overload to trip.
Can anyone comment on this? If my theory is correct, I would look at sizing the overloads more conservatively and, in the future, specifying motors that have internal thermal protection. I assume the 100 kva generator is sized sufficiently.
Thank you!
On 2 occasions, 2 different motors were locked up due to an ice blockage - one single phase motor operating an auger and one 3 phase motor operating a cutter assembly. The motor overloads did not trip (fuses in the case of the single phase motor and overload relay in the case of the 3 phase motor). Instead, the motors just started heating up in a locked condition. Luckily, I was able to find that the motors were stalled and I shut off power before the motors burned up. In the process of troubleshooting why the motor was not running, I checked the voltage. It was "pulled down" to 165 volts.
My theory on this is that there is not enough power in the supply to maintain the voltage to a sufficient level to allow the motor overload to trip.
Can anyone comment on this? If my theory is correct, I would look at sizing the overloads more conservatively and, in the future, specifying motors that have internal thermal protection. I assume the 100 kva generator is sized sufficiently.
Thank you!