As DPC stated the MCA is 125% of the largest motor plus the sum of the remaining motors/loads on the unit. This is used for sizing the feeder. The MOCP is generally 225% of the largest motor plus the sum of the remaining motors/loads on the unit that is used to determine the upper limit of the overcurrent protective device which may be selected.
You will also see from some manufacturers, the "RLA" given, which is "Running Load Amperage", which is the actual expected running current under normal operating conditions. This would be what we include in our load summaries.
Regards,
EEJaime