motor heat exchangers

Status
Not open for further replies.

monjo

Electrical
Jan 15, 2004
5
Have a problem with dust buildup inside tubing of large motor's heat exchanger. Want to have measurements of air velocity/ flow into and out of exchanger to use as an indicator that tubes may need cleaning. Could someone reccomend any sensors/ probes etc which may be used? Has anyone used similar, and where would you mount them?
 
Replies continue below

Recommended for you

hello
Try to place two manometers, one on the inlet flange, the other on the outlet flange, air side.
Verify with the heat exchanger data sheet the pressure drop of the component, as indicated by the supplier.
then, if the pressure drop are higher than declared, your heat ex. has to be clean.
If You nead a continuos registration, for istance to give indications to the plant operators, you can use a pressure differential trasmitter, i.e. two pressure transmitter devices connected together.
In any case, if your H.E. is dirty, on the secondary side you should have less temperature (at the secondary side outlet) than usual, or guaranted (obviously if your HE works at the design conditions, with reference to primary and secondary flow and inlet primary and secondary temperature)
I hope to be helpfull....
Bye
Engy74
 
if dust is the problem, then filter the air.

also, with fairly good assumptions, that is process flow rates are steady-state, then by monitoring temps alone will provide you sufficient information as to the exchanger's performance.

good luck!