Have a problem with dust buildup inside tubing of large motor's heat exchanger. Want to have measurements of air velocity/ flow into and out of exchanger to use as an indicator that tubes may need cleaning. Could someone reccomend any sensors/ probes etc which may be used? Has anyone used similar, and where would you mount them?
 
Replies continue below

Recommended for you

Suggestion: Please, also post this in Mechanical Engineering Section of this Forum.
Pitot tubes may be considered. They may be installed in ducts.
 
How about measuring dp.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
Use a Differential Pressure Gauge. This type of gauge measures the differential pressure across two different areas, usually the inlet/outlet of filters. If the pipes congest, the difference in pressure in/out will increase. Regularly these are in the range of 0 to 8 inches of water pressure and some include auxiliary contacts.
 
Take a look at the Dwyer Magnehelic DP gauge/switch. They are an anlog device with a gague reading acturl pressure and a "red line" needle that sets the alarm point. You can see the trend as the DP rises toward the set point.
 
Pressure switch at the inlet air, flow switch at the outlet, and temperature switches at the inlet & outlet are the standard instruments used for large machines. We can deduce leakages, chockages, excess heating in the motor etc
 