rockman7892
- Apr 7, 2008
- 1,176
I have an application where 12.47kV switchgear has a feeder breaker which feeds a motor that has a captive transformer with the transformer secondary and motor operating at 4.16kV. This motor is a synchronous motor.
The existing Switchgear is being replaced and an SEL-710 relay will be used to provide motor protection. It is being requested that motor differential protection be included and that the differential zone extend from the motor neutral point all the way up to the line side of the feeder breaker (not core balance CT's at motor).
Does anyone have any experience with this type of application or know of any pitfalls to look out for? My initial concern is how to account for the phase shift across the Delta-Wye transformer that will be in the zone of protection. With a dedicated transformer differential relay you can program the relay to account for this shift but with this motor protection relay there doesn't appear to be that option. The only thing I can think of would be to wire the two sets of CT's in wye and Delta respectively in order to account for this shift external to the relay?
The existing transformer is LRG on the secondary to 400A. The CT on the transformers secondary neutral will be connected to the ground input on the relay. Are there any issues of using a CT on the transformer secondary for ground fault detection in a motor relay?