I have been asked to do a review of an incident at a site that occurred over 6 months ago and where the site conditions have changed considerably since. The information gathered from the site, by others, during the events was sparse.
The site has a 2 pole, 400V, 30 kW pump which was used to pump water into an uphill filling tank. The motor was controlled by a Danfoss MCD 202-030 soft starter, these soft starters have thyristors installed on two out of the three phases (red and blue). The configuration had experienced multiple instances of fuses failing. The original fuses were rated at 160 amps, type unknown. These were eventually upgraded to SIBA aR model 20 282 20.180 (180 amp) fuses, in line with ratings shown in the Danfoss manual.
After the fuse upgrade the soft starter began blowing thyristors on the Blue phase during a ‘soft stop’. Monitoring was placed at the site which indicated that the Blue phase voltage was falling significantly, upstream of the soft starter, whenever a soft stop was initiated. This fault occurred on at least four occasions.
The theory that was presented was that the site would be running at a small load, a soft start would be initiated, and the pump would start up without any issue and the internal bypass contactor within the soft starter would short out the thyristors. The pump would then operate for around eight hours and at that point the pump would be asked to stop. The theory goes that during operation there was a ‘dry joint’ type connection, on the blue phase, upstream which would heat up, and when the soft start was initiated the increase in current of around 400% full load current would cause a voltage dip then causing even more current to flow to the motor. This high current was enough over a few seconds of interval to cause the blue phase thyristor(s) to fail. That’s the theory that I’ve been asked to investigate.
Unfortunately, I’m not a motor person
. So, my question is, what does the current into a motor do when a soft stop in called for under normal operation? I can find plenty of sources which will show what happens to the current during soft starting of a motor, but have been unable to locate a graph showing the same for a soft stop. Do I have a 400% increase in the current during a soft stop when the pump would still be under some load? If that is the case would there be some equation I could use to estimate the current maximum during this operation?