A 480 volt, 3 phase motor control center for one of my chillers experiences frequent tripping on 3 of the starter controllers if the panel doors are shut.
Our Chief Electrician's answer to this problem has been to prop the panel doors open and direct a large fan on the panels.
This condition has existed for the 6 years I have worked here. In my mind, 480 volt panel doors left open present a serious safety risk and increase the potential damage from possible arc flash. I have never witnessed any form of preventive maintenance performed on these cabinets or any of our switchgear.
I also noted we have a rather large voltage/amperage imbalance indicated on two of my chiller control panels....The remaining chiller panel does not offer volt/amp indications. The imbalance varies up to 10-12 volts and 60-70 amps between phases.
We have also experienced frequent motor failures on tower fans and pumps.
A few months ago one of our older hermetic chillers experienced a motor burn out. We replaced the chiller and MCC, but still have large volt/amp imbalance at chiller.
This is a Federal facility.
I need help building my case to prove all these conditions are related, and most likely caused by lack of preventive electrical maintenance and deterioration of switchgear.
I am not an electrican, so please advise what is considered good engineering practice in reqards to preventive maintenance on this level of equipment.
Thanks Gents!
A 480 volt, 3 phase motor control center for one of my chillers experiences frequent tripping on 3 of the starter controllers if the panel doors are shut.
Our Chief Electrician's answer to this problem has been to prop the panel doors open and direct a large fan on the panels.
This condition has existed for the 6 years I have worked here. In my mind, 480 volt panel doors left open present a serious safety risk and increase the potential damage from possible arc flash. I have never witnessed any form of preventive maintenance performed on these cabinets or any of our switchgear.
I also noted we have a rather large voltage/amperage imbalance indicated on two of my chiller control panels....The remaining chiller panel does not offer volt/amp indications. The imbalance varies up to 10-12 volts and 60-70 amps between phases.
We have also experienced frequent motor failures on tower fans and pumps.
A few months ago one of our older hermetic chillers experienced a motor burn out. We replaced the chiller and MCC, but still have large volt/amp imbalance at chiller.
This is a Federal facility.
I need help building my case to prove all these conditions are related, and most likely caused by lack of preventive electrical maintenance and deterioration of switchgear.
I am not an electrican, so please advise what is considered good engineering practice in reqards to preventive maintenance on this level of equipment.