Nope. I'm sorry, not being sarchastic.. I knew this would open a can of wormies.
It of course depends on the application. For a 5-10hp motor running an air or refrigeration compressor I would use anything BUT heater-type overloads. I have seen so many that have damaged the motors under their protection. As I mentioned, so have whole industries, like refrigeration. They are so bad I've started thinking they were created for service companies to make money with. They need to have their screws checked often. They get warm and corrode. Often when malfunctioning they resort to causing single phasing.
This is as relates to all the ones I've seen. I haven't come across the new ones with blade heaters etc. etc. Maybe they work okay.. I have no direct experience with them.
I can say it is very, very, hard to tell the owner of a Maw&Paw grocery store that they need a new $1,500 compressor because the protection device fried it. They get kinda
![[mad] [mad] [mad]](/data/assets/smilies/mad.gif)
.
Also fused service disconnects cost way too much for what you get,(regular single phasing!), compared to a pure disconnect.
If I were ian4340 I would use a non-fusible service disconnect and a breaker on that motor. I would however go to the effort to find a HVAC breaker!
If I wanted more protection I would use a motor monitor to condition a contactor.