If you have a bus with:
6 income generators
3 big mill motors fed off of it
and 1 interconnector running through a transformer to another bus
And if there is a fault on that interconnector, then to calculate the fault level I understand that you calculate the contribution of the generators, but in respect to the motors, won't their contribution be negative?
The way that I'm thinking, is that they will draw current away from the bus in normal operation, which they convert to inertia in a certain direction of rotation. Now when that supply to the motor is withdrawn, won't the inertia of the load induce a current flow in the motor that is associated with that direction of rotation? (which of course is still in the same direction - out of the bus)
So, to calculate the fault level on that interconnector, won't i calculate the contribution of the generators and then subtract the magnitude of the contribution of the motors?
Thanks for your guidance,
Matt.
6 income generators
Matt.