Dear Mr. beyond86 (Electrical)(OP)10 Dec 22 12:07
" #1....When we perform SC calculation, should taking into account motor contribution current from LV motors (0.4 kV or less) or only from MV motors?"
1. All motors LV and MV (except those connected to simple VFD ) do contribute "motor-feed back" during short-circuit. Therefore, motor contribution current shall be taking into account on SC calculation. There are conditions and recommendations, see 3.
"....#2. I calculate SC at 110 kV bus,.... many LV motors 0.4 kv connected to transformers of 10/0.4 kV, then transformers 35/10 kV and then 110/35 transformers...."
2. All 0.4kV motors do contribute to short-circuit current during short circuit. But are you considering its contribution to 110kV bus ? The answer is NO. See 3.
"....#3. In which standard I can find information about this? "
3. In the IEC world, IEC 60909 covers this very well.
Che Kuan Yau (Singapore)