guilio2010
I'm going through old notes to remember 3 phase motors and it's not making sense and didn't know if I could get this cleared up.
If I have a 7.5hp motor, 5.6kW, 3 phase. We'll assume .8PF and .9eff
Voltage 480V, 277V LN
In single phase:
I = 5.6 / (480 * .8 * .9) = 16.2 A
This is 7776 VA (480 * 16.2) which multiple by .8 PDF and .9 eff, you get 5.6kW.
In 3 phase
I = 5.6 / (480 * .8 * .9 * 1.73) = 9.4 A/phase
From here I'm trying to do the check. To make sense of this, is the total power divided by 3 for each phase? Then from calculated above, 9.4 x 277 = 2602 VA and to check 5.6/3/.8/.9 = 2592VA?
Also, if the motor is operating at full power, is the 3 phase motor operating at 16.2A but because 3 phase power, one leg is at 9.4 A and the other two legs at 3.4A? Will using 480V give you the full draw of the motor instead of using Vln?
Thanks,
Guilio
In single phase:
In 3 phase
Thanks,
Guilio