Dear Mr. Jk1996 (Electrical)(OP)
@ all NEC user community
1. Reference: As per NEC NEC 430-6 (a) (1) " the values shown in Tables 430-147....150 shall be used to determine the ampacity of conductor.... , instead of the actual current rating marked on the motor nameplate..... Exception No. 3: For a listed motor-operated appliance that is marked horsepower and full-load current, the motor full-load current marked on the nameplate of the appliance shall be used instead of the horsepower rating on the appliance to determine......"
NEC Table 430-149 " ..... Motors built for especially low speed or high torques may require more running current, multispeed motors will have full-load current vary with speed, in which case the nameplate rating shall be used...."
2. Following is my personal opinion. All learned advice are greatly appreciated and welcome.
2.1 The values shown in Table 430-147.....150 are assigning a "fictitious" current value based on standard horse power rating, taking the phases, voltage rating only.
2.2 If the actual current rating marked on the nameplate is taken:
a) the value would be the "actual" input current value which would had taken into account of the Power (hp/kW), whether it is a single or three-phase, rated Voltage, rated
Frequency, rated Speed (RPM), rated Power-factor, rated Efficiency etc.
b) it would replace Table 430-147 ....150, which would be superfluous.
Che Kuan Yau (Singapore)