toygasm4u
Electrical
- May 17, 2006
- 37
I've hit a brick wall with a Baldor 1HP motor and a Delta VFD"E" series drive. For a 460V blower application, I want to run the motor at 10~60 Hz. The motor is rated 10:1, and my PWM is set to 15kHz. When this motor is running between 10 and 15 Hz, it cogs. This cogging is translating mechanically through the equipment, making a not so pleasant noise; the carrier is also bumped down to the 4-8 kHz range. Beyond 15Hz, this thing operates as expected; smooth and quiet.
I've tried swapping between Vector and V/Hz mode, and performing an Autotune. For V/Hz mode, I tried setting my midpoint voltage at 230, and my midpoint F at 35Hz, (plus several other combinations). I've also verified that the drive isn't trying to inject any DC braking at the lower frequencies; I just turned those features off. I can't seem to null this cogging out, or even make a dent in it.
Any insight would be greatly appreciated,
~M
I've tried swapping between Vector and V/Hz mode, and performing an Autotune. For V/Hz mode, I tried setting my midpoint voltage at 230, and my midpoint F at 35Hz, (plus several other combinations). I've also verified that the drive isn't trying to inject any DC braking at the lower frequencies; I just turned those features off. I can't seem to null this cogging out, or even make a dent in it.
Any insight would be greatly appreciated,
~M