motor 50 or 60 hertz 1
horse56
Industrial
I am new to this site and I have a question about a motor being 230 volts 50HZ being sent and used in Hong Kong where there electric is 50HZ and 220 volts. The motor would be purchased from Graingers in the US. I heard that the power overseas has one hot leg and in the US we have two hot legs. So this has led me to some confusion. The power in the US has two 115 legs and they have one 220 leg.
The important thing is what the motor sees. It doesn't mind if wires are "hot" or not. All it cares about is the voltage difference between the two wires. Motors don't get "confused" by words.
As long as the ratio volts/frequency is OK, the motor will do its work. So, if you have a 230V/50 Hz motor, the V/Hz is 4.60.
Now, if you connect to 220V/60 Hz motor, the ratio will be 220/60, which is 3.67. That is too much off the ratio the motor was designed for. So it will not work well.
But, if your voltage is 220V/50 Hz, the ratio is 4.40 and that is OK. The motor will work well. The tolerance is usually +/-5 %. So any ratio between 4.37 and 4.83 would be OK.
Gunnar Englund
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...
Hello folks, are the theory involved applicable to power transformers as well since the equivalent circuit of an induction motor is almost the same of that of a transformer?
GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata
In a very broad sense, yes. But, since there is a variable called slip involved, you cannot do anything useful with the basic transformer formulae.
Gunnar Englund