StructureMan44
Structural
- Dec 10, 2014
- 201
An existing 6in slab is poured directly on beams at 5ft spacing without decking (the original contractor must have used removal/reusable formwork). The top of the beam flanges are embedded .75in inches into the bottom of the slab without shear studs resulting in a 5.25in deep slab over the beams. We need to remove the slab in some areas and replace it with 1.5in deep grating (I assume you can saw cut concrete directly over the flange of a beam?). This leaves a gap of 3.75in between the top of the beam flange(s) and the bottom of the welded metal decking. 1.5in deep decking is used to match the decking on the rest of the project.
What is the most efficient way to fill this 3.75in gap while also providing support for the metal decking? I am planning on having the contractor weld an HSS3.5x3.5x1/8in running parallel to the beam directly to the top of the beam flange and then weld a 1/4in plate on top of the HSS section. Is there a more efficient way to do this?
Also, is there a way to calculate how much load an HSS section can take compressing two opposite faces and is there a way to calculate if 1.5in is enough bearing distance for the metal decking?
What is the most efficient way to fill this 3.75in gap while also providing support for the metal decking? I am planning on having the contractor weld an HSS3.5x3.5x1/8in running parallel to the beam directly to the top of the beam flange and then weld a 1/4in plate on top of the HSS section. Is there a more efficient way to do this?
Also, is there a way to calculate how much load an HSS section can take compressing two opposite faces and is there a way to calculate if 1.5in is enough bearing distance for the metal decking?