the test ASTM 780 is the field test for sampling mortar for compression testing. It states in bold letters to not use it for mortar acceptance. the test for mortar acceptance are C270 and C109. the lab test is run on a controlled sample of mortar cement (or masonry cement) on a proportioned amount of mortar sand and water. The acceptance test for mortar has nothing to do with what's going on in the field. mortar is deemed acceptable by testing performed on silos of cement by the manufacturer. imagine if the same were true for concrete....
Here's the deal... ASTM use to stand for American SOCIETY for Testing and Materials, before it became ASTM International. This society is made up of members from all industries and the standards and tests go through a consensus approval and revision method. ASTM has proportionally speaking very few members who are involved in the testing for acceptance business. There are a lot of members who are involved in manufacturer QC. C780 is the best the consensus can come up with. I would personally like to see everybody get together and agree to a REDUCED ACCEPTANCE psi for both batch samples and board samples of field sampled mortar.
Here's the dance:
1.Master spec calls for C780
2.Designer (Arch, Egr, or the Secretary) leaves it in
3.Testing company takes a sample and it fails
4.Everybody starts to question constructed walls
5.The contractor takes the position that the test is invalid. Which may occur only after they have spoke with their mortar cement supplier. This means cutting prisms of constructed masonry will be taken off the table (unless you want a big change order)
6.Walls stay. No more mortar is tested. Testing company looks like a bunch of jacka$$es.
Here's a concept for design professionals out there that use the ACI masonry code in their design.... Why are you specifying so much testing? Most projects i see have Level 3 Masonry TESTING and Level 1 Masonry INSPECTION. Taking samples every 5000 sqft of wall is a LEVEL 3 testing requirement. Level 3 INSPECTION requires CONTINUOUS observation of block placement, mortar joints, and obviously the grout....My most intensive masonry projects require Level 2 inspection (periodic block, joints, reinforcing, and continuous grout), however the testing requirement by code for LVL 2 is met by pre-construction testing.
back to the point... wayniac3 should go back to the site with a camera and observe mortar batching. If there is no box (1 ft3) to measure sand, document it on your field report and take a photo of the shovel guy. If there is no box, the design team will have more leverage to demand saw-cut prism testing.
If i were on the design team, i would view it quietly as acceptable... but make a stink about it to keep the masons on their toes about proper batching.