jheidt2543
Civil/Environmental
- Sep 23, 2001
- 1,469
I was looking at this old thread:
and I’m wondering if anyone has seen any more follow up on it?
J1D notes:
“From the guide, the force and bending moment equilibrium equations at the plate-to-base interface are (page 21):
T+P=fp*A*B
P*A’+M=0.5*fp*A*B*(N’-A/3)
The dilemma is that negative (compression) values of T (anchor force) were obtained when loads (P, M) have large eccentricities.
Let’s take Example 16 (page 23) as the example, but change Mu to be 480kip.in. Then Pu=88kips, Mu=480k.in --> e=5.45in >N/6 = 2.33in (limit of full compression)
Therefore, part of the base plate will be separated from the base and the anchor bolts must be in tension.
However, the outcome is: A=4.04 --> T = -0.16kips (compression)
This can be proved more easily by a Spreadsheet or MathCAD. Keep changing Mu, you’ll find there is a theoretically tragic zone. The results fall apart and are contradictory.”
I have looked at the paper “Inconsistencies in Column Base Plate Design in the New AISC ASD Manual" and it presents an alternative equation, which I will be working through. I’m just wondering if others have run into this and what you may be doing about it.
and I’m wondering if anyone has seen any more follow up on it?
J1D notes:
“From the guide, the force and bending moment equilibrium equations at the plate-to-base interface are (page 21):
T+P=fp*A*B
P*A’+M=0.5*fp*A*B*(N’-A/3)
The dilemma is that negative (compression) values of T (anchor force) were obtained when loads (P, M) have large eccentricities.
Let’s take Example 16 (page 23) as the example, but change Mu to be 480kip.in. Then Pu=88kips, Mu=480k.in --> e=5.45in >N/6 = 2.33in (limit of full compression)
Therefore, part of the base plate will be separated from the base and the anchor bolts must be in tension.
However, the outcome is: A=4.04 --> T = -0.16kips (compression)
This can be proved more easily by a Spreadsheet or MathCAD. Keep changing Mu, you’ll find there is a theoretically tragic zone. The results fall apart and are contradictory.”
I have looked at the paper “Inconsistencies in Column Base Plate Design in the New AISC ASD Manual" and it presents an alternative equation, which I will be working through. I’m just wondering if others have run into this and what you may be doing about it.