Has anyone come across a method to determine the capacity of a concrete hollow beam.
With a rectangular beam, the concrete stress block is quantified as (0.85.f'c)(γ.ku.d).
I can understand the "0.85.f'c" part but what would "γ" be?

The beam is rectangular and the void is rectangular.
 
Replies continue below

Recommended for you

Gamma is the same as usual. The trick is that the width changes if the compression zone extends below the top flange, into the webs.

Look up T-beam examples (or flanged I-beams) online or in a text book. It's the same principle. The total width of your two webs is substituted for the stem width of the T-beam.
 
OK thanks I'll give this a try.
 