Thank you Erdbau and ishvaaag. Interesting note...In the Micropile Design and Construction Guidelines, they recommend that a factor of safety of 2.5 be applied to grout/bedrock bonding strengths. By contrast, the Drilled Shaft Manual published by the US DOT for caissons indicates that for a caisson drilled into a moderate bedrock, an allowable bonding strength of 3 to 5 percent of the concrete compressive strength can be considered. On face value, this would lead you to believe that allowable bonding strengths are greater for the caisson than for the bored micropile.
To add fat to the fire, a rock anchor may be designed for higher bonding strengths, but rock anchors are routinely tested. In bored micropile applications, this is not always possible.
Any thoughts?