Minimum thickness for concrete pour 2
JoeBaseplate
204
Is 1” too thin a thickness for concrete slab on grade (using fibermesh)? It’s an odd situation, the pour thickness slopes from a 3” at one end to 1” at the other with aprox 4 ft width across. The pour is going to be on top of an existing concrete floor (basement underneath). The concrete floor has been roughened to a ¼” amplitude. The pour being suggested is 3/8” chip mix with 5” slump and no fly ash (all cement). The floor will get tiled or carpeted eventually.
So is 1” too thin a thickness to pour?
You said it was a slab on grade, then said it is poured on an existing slab with basement below. Which is it? What you described is a topping. I would leave out the plastic fibre, as it will do no good. Otherwise, sounds doable.
hokie, sorry for the confusion. Its not a slab on grade but rather a floor infill.
You need to spec a concrete with approprate sized agg and contents, the concrete supplier should be able to help you out here.
ANY FOOL CAN DESIGN A STRUCTURE. IT TAKES AN ENGINEER TO DESIGN A CONNECTION.”
Can you not apply a chemical bonding agent on top of existing floor that will ensure that the whole depth acts as one to take any point loads ?
normm,
The best "chemical bonding agent" is Portland Cement. With the other stuff, there is too much chance that it will act as a debonding agent.
Update:
The topping may actually be 1"-1/2" thickness and now I am wondering if I should just have them use non-shrink grout.
Surface preparation is critical for success. The surface may have been roughened to 1/4" amplitude but how has it been cleaned (water blasting, sand blasting, shot blasting?
A portland based sand/cement slurry can be an effective bonding agent as long as the surface has been prewetted (no ponding water) and is scrubbed into the surface. For thin cementitious toppings I am a fan of matching the properties of the base slab.
Joe's topping strip is only 4 feet wide. Why the big issue with preparation? He's not depending on composite action as far as I know. Joe, just use the small aggregate concrete as intended. Non-shrink grout is overkill in this case and not the best solution.
Joe, do not use grout!!! grout is designed to be contained between surfaces. Use one of the commercial polymer modified topping materials.
Michael.
Timing has a lot to do with the outcome of a rain dance.
Indoors, non-load bearing. Or am I interpreting the statement wrong?
Can he just use a floor-leveling compound?
No, floor leveling compounds are for small irregularities, not 1.5 to 3 inches. Nothing better than concrete.