I am gonna be more precise.
This is an MSE wall about 8 m high composed of crushed tuffa excellent fill material , something you guys would classify as A-1-a. the contract specifies modified proctor references while i used to believe that a standard test would be enough especially since there will be no vehicles circulating above the wall when the project is delivered. Vibratory equipment is prohibited since the MSE function is to protect a small cliff harboring an archaeological site from falling .
I made the preliminary decision of accepting about 90% of the modified Proctor MDD.
Edit: iv'e checked out some pdf on the net and some of them recommand using 95% from the T-99 AASTHO for slopes and walls and 100% for walls supporting foundations