Minimum inspection requirements for precast structures

Status
Not open for further replies.

EndBayTurn

Structural
Aug 17, 2005
5
I'm looking for the minimum weld inspection requirements for precast structures, in terms of what needs to be inspected and the frequency of inspection. It appears to me that AWS requires all welds to be visually inspected, however it doesn't specify a frequency for other types of inspections, such as dye penetrant or mag. particle. The code I am using is 1996 BOCA, but it refers to AWS.

Are there minimum requirements that I am just not seeing? I am trying to determine if what I require in my specification is more than what the code minimum requires. Any help would be appreciated.
 
Replies continue below

Recommended for you

Some points to consider:

1. You are right about the requirement for VT during all phases (before, during and after) of the welding process. This will certainly satisfy minimum code requirements and provide greater safety. D1.1 Section 6.9 requires VT of all welds. If Chpater 17 of the NBC does not have a provision which allows for a lower frequency, than I presume that is what you'll have to go with.

2. According to D1.1 Sections 2.20, 5.26.1.4, and 6.10, MT and PT will not be required, except for determining the extent of cracks in welds.

3. If there is welding of rebar to structural steel involved, welders and WPSs will have to be qualified to both D1.1 and D1.4. See also PCI MNL Article 2.3.1

4. In addition to NBC Chapter 17 which references AWS D1.1, useful references are D1.1 Section 6 Part A and Table 6.1, PCI MNL 116 Article 2.3 and IBC Table 1704.3. The IBC does allow for periodic inspections of certain welds while D1.1 Sections 6.9 and C6.9 do not. I included the IBC Table because it clearly elucidates the different items which require inspection; something you can modify to suit your needs and still meet BOCA requirements.

 
I read that RI's building commission adopted the 2003 IBC last July. When will building departments in the state start requiring that building structures be designed according to IBC provisions?
 