I did calcs for a long building which required existing hallways to be upgraded to 1-hour fire resistance.

Since these walls were being re-paneled anyway, I used the shear resistance to qualify the resisting capacity of the building.

The walls sit on a 4" slab.

The entire slab is surrounded by a 12" below grade perimeter footing. So, I can qualify the bearing beneath the slab as 1500 PSF, and the walls have only 100 PLF.

Does anyone foresee problems at review? It was submitted today.
 
Replies continue below

Recommended for you

The only problem I can see is with the required 3" clearance from the soil to any reinforcing steel, to include thge anchor bolts. Normally I thickebn the slab under ther shear wall to 8 to 12" to accommodate this.

I assume with a long wall that holddowns were not needed and that if seismic governed for the gyp that you used half sgtresses for the shearwall capacity?

Mike McCann
MMC Engineering
 
what the shear resistance has to do with fire resistance? where is the shear resistance came from, by reinforcing dowels? Sorry, I don't understand your question.
 
msquared,

That is a good mention. I thought of it in process, then forgot it.

Using IBC 2006 Table 1911.2, I can spec .25" dia. bolts @ 4' o.c. (500# shear allow). The embed is only 2.5", leaving 1.5" clear.

Plus there is a vapor barrier.
 
In the end, I changed my shear distribution almost entirely to proposed wall sections. Where I had to distribute to existing walls, I spec'd powder driven nails at 6" o.c.
 