Minimum flowrate in IX water softening to prevent channeling

Status
Not open for further replies.

PEDARRIN2

Mechanical
Joined
Oct 1, 2003
Messages
1,287
Location
US
I am looking for a guideline minimum flow rate of water through a ion exchange water softener which will prevent channeling.

I have seen the guideline of 1 gpm per ft3 of resin - but want some verification.

The application is for individual facilities, not central utility treatment, if that makes a difference.

 
1 gpm per cubic foot of resin is a better number than the RH suggestion. Our recommendation is 8 - 40 BV/h. 1 gpm/ft3.

Gary Schreiber, CWS VI
The Purolite Co.
 