bobinillinois
The 2007 NFPA 13.8.6.3.3 says that sprinklers shall be located a minimum of 4" (102mm) from a wall.
My state's architect responsible for Life Safety has said that his interpretation of this is that the deflector must be at least 4" from the wall. Based upon the width of different sprinkler deflectors that can move the center point of your sprinklers some distance one way or the other.
I've discussed the same issue with one of the "ask the expert" folks who disagrees with this interpretation. His take on it was that based upon figure 8.6.4.1.1.3 the distance is to be measured from the wall to the center of the sprinkler.
I tend to agree with the architect's interpretation as the code says "sprinklers" must be a minimum of 4" from a wall, not the "center of a sprinkler" or "a sprinkler's element."
What say you?
What say you?