The Westinghouse T&D Reference Book (Chapter 3, IV Corona, pp. 56-62 in 4th edition) gives an equation somewhat different from Magoo's Peeks equation.
Eo = go·delta^(2/3)·r·m·ln(D/r)
where
Eo=critical disruptive voltage in kV to neutral
go=critical gradient in kV per cm (21.1 kV/cm, but Section 10 gives more accurate numbers and includes bundled conductors)
delta = air density = 17.9·b/(459+°/f)
b=barometric pressure in inches of Hg
r=conductor radius in cm
D=distance in cm between conductors for 1Ø or equivalent Ø spacing for 3Ø
m=surface factor (0.82 for stranded, 0.92 for segmental)
It also has corona loss curves for different conductor types.