Thank You for your impute. We asked our safety dept. to come on site they did this is there recommendations.
A thorough job briefing must be performed, identifying any and all hazards associated with each individual manhole.
Each crew member must know the name of the circuit being worked on, as well as the exact location of the manhole being entered.
Prior to entering the manhole, a thorough visual inspection of the cable must be performed. The employees must ensure that the conductive sheath and the ground connections are not disrupted. If any of the static wires near the elbows are broken or disconnected, they must be repaired if possible.
Arc suppressant blankets should be used where possible to prevent injuries, should an unexpected equipment failure take place.
In addition to the arc blankets, rubber protective blankets should be used, where necessary, to prevent employee contact with the energized conductors.
Dielectric boots/overshoes, rubber gloves and rubber sleeves should also be worn when working in the manholes.
Additionally, I recommend that additional layers of FR clothing or PPE be worn when entering the manholes. It is also advisable that employees wear arc rated faceshields when moving/manipulating cables in the manholes.
I have explained to my employer the problems Oyster Creek Generating Station had with the same type of cable.
The independent failure analysis and the root cause analysis prepared by AmerGen determined that the May 20, 2003, cable failure was the result of water intrusion into the Ò1CÓ cable between the insulation and the insulation shield. Apparently, underground water filtered through the conduit and cable jacket, degrading the cable insulation and causing the cable to short to ground. The cable that failed in May 2003 was manufactured by Anaconda. Prior to this event, Oyster Creek had experienced an additional ten inservice, medium voltage cable failures. Of these, six were failures of Anaconda Unishield type cables. A seventh failed cable was also Unishield type manufactured by Cablec, after their purchase of the Anaconda company. Based on a chart prepared by the licensee, the Anaconda and Cablec cable failures were either due to water intrusion or manufacturing defects that, over time, caused the cables to fail.
I have asked for FR ear plugs. I don't want to be blind and deaf.
This type of cable appears to have no fault carrying capability. And after a number of faults along with the age of the cable I believe the integrity of the cable is bad at best.
Regards Deltay