born2drill
Geotechnical
I'm looking at a micropile project with design loads of 200T in compression and 220T uplift. These piles would be cased to rock with the threadbar grouted into a socket below.
In the past I have seen other engineers limit the strength of the reinforcing to 87 ksi, based on limiting concrete compressive strain to 0.003. This approach is mentioned in FHWA's Micropile Design & Construction Guidelines, section 5.E.7.
Should this prohibit me from relying on high strength (150 ksi) reinforcing steel for a rock socketed micropile? The grout will certainly have confinement in both the cased and uncased sections, so is the grout crushing or fracturing really a legitimate concern?
I'd be interested to hear if anyone has designed micropiles using bar strengths over 87ksi. It seems the geotech engineer on the project who will be doing the review is fine with using 150 ksi steel, but I'm still interested in hearing some outside opinions.