Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Micrologix 1200 and a 1762 IT4

Status
Not open for further replies.

hollycrap

Electrical
Joined
Jul 17, 2009
Messages
1
Location
US
Newbie to this and was wondering if anyone has had problems setting up a RTD input card to a 1200 processor. I have version 5.x software and it dosen't see the card when you do a I/O config.I set it up via other card with the 5 word file but I do not get anything reading on my input file or errors so I know the card isn't enabled. What other files do I need to make a PID to track a water temp and adjust it with my analog output? Any help would be appreciated.

Mark
 
I use IR4 cards with ML1200's all the time, a few minor issues.

First, you have to select the card from the menu and add it to the I/O, not sure why but I've never had much luck with the Read I/O Config on the MicroLogix. The go to Adv Config and enable the channels you want, and set the display parameter, filter and such.

Go to Processor Status, and on the errors tab, set a "1" into S:1/8, Fault Override at Startup. Otherwise if you have a small program you can get an I/O fault during powerup.

Hope that helps.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top