Depending on the process ozone (can be operated in combination with UV) or low chlorine will do the job. It is however also important to look at the process circumstances which cause MIC. First of all there is the temperature. Unfortunately, this cannot be controlled since it's a process parameter of your cooling system. Cooling water systems usually have the right temperature for microbiology. The second one is flow. Microbes preferably settle in places with low flow speeds. Prevent your water system being stagnant. Third there is "food". Low TOC-levels (do you use RO-water in the cooling system ?) mean little biological growth. Finally there is oxygen. If there is dissolved oxygen, the anaerobic micro-organisms which cause MIC will not grow. Beware however of anaerobic spots in your system. If you have a completely closed cooling system, it probably will be completely anaerobic.
If biocides are used, it might be interesting to think about shock treatment. A shot of chlorine once a week has more effect than continuous dosage and is less expensive. However, do not use this in a system which already has a lot of biofouling, a lot of rubbish will detach from the metal surface and will enter your cooling system. There are interesting tools available to measure both active chlorine and biological activity on-line such as the Biotox of CESI. These can be used for process control when using bio-shock treatment.