That's vague. If they are talking about the incomer, that assumes CT has to have metering accuracy. but if you are talking about relays then I agree with RRaghunath.
You need to confirm if they are talking about:
1) SCADA matering (IED function is enough)
2) Revenue metering (metering class/accuracy CT needed)
3) if yes to 2), confirm CT is revenue metering approved (region dependent).