NorEE

Electrical
Oct 3, 2011
25
Hi to all,

I would just like to ask your inputs with regards to the metering readings in the attachtment.

What problem does this reading pose?
What are the possible causes?


Any input is well appreaciated.


Thanks!
 
Replies continue below

Recommended for you

To save everyone the trouble, the contents of the file are below. There's no need to download the file or to run Excel.

Metering From LCD

IA = 136.8A @ 150deg
IB = 136.4A @ -150deg
IC = 136.8A @ 90deg
IN = 0A @ 150deg
IG = 262.8A @ 149deg

VA = 7.77kV @ 0deg
VB = 8.02kV @ -121deg
VC = 7.94kV @ 121deg
VS = 0.226kV @ -166deg

I1 = 45.1A @ -30deg
3I2 = 271.6A @ 150deg
3I0 = 261.4A @ 149deg

V1 = 7.92kV @ 0deg
V2 = 0.013kV @ 161deg
3V0 = 0.422kV @ -154deg

Power Factor
A = -0.86 lag
B = 0.87 lag
C = 0.85 lag
 
That you need to swap the polarity of IA?
 
I'd be looking to reverse IA too.

It will be causing power to be recorded incorrectly.
 
Another vote for turning IA around.

Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
I agree with the Ia polarity issue. What is the expected direction? All currents are shifted 180 deg, which may be entirely accepted for the application, but worth pointing out.
 
LiteYear,

Thanks for the favor, well appreciated.



To all who replyed, thank you.


We'll be checking connections by the earliest possible time - plant in operation right now.




smallgreek,

Application is protection relaying w/ SEL 351 sir.
 
If you are using any of the Directional (67) elements of the SEL-351, best to get your phasing sorted asap.
 
If you are concerned about Watt/Var direction, this could also be a concern. Ie, generators consider +Watts to be one thing, feeders, another. Find out if you are concerned about consuming / producing watts/vars. It may be the case that all CT's are reverse polarity, in addition to the Ia polarity issue.
 
rterickson,

sir, as per setting, 67 elements are disabled. i will verify this setting with designer asap.

Thank you.


smallgreek,

thank you for pointing that out sir, i will also confer this to the designer.

Lots of thanks!
 