Folks,
I have never worked much with calculating the capacities of bare metal decks and have a question.

I was recently reviewing a report where the shear capacity of a CF46 Metal deck ( was calculated to be 16.1 MPa (2.335 KSI). It was mentioned that "shear buckling" controlled the capacity.

Where can I find information regarding how to calculate the capacity for metal decks?

We are Virginia Tech
Go HOKIES
 
SDI's Diaphragm Design Manual is the industry standard for these calculations and provides information regarding shear buckling - it can be ordered here:
As mentioned in a previous post you can also use Hilti's Profis DS program to determine shear strength of metal decks (including output for panel buckling/shear buckling strength) that match the Diaphragm Design Manual. Download here:

 
I attach a pdf of a Mathcad 2000 worksheet for the calculation of the strength of trapezoidal deck sections. Therein the formulas for web crippling and strength are extant. Since it is maybe 10 years that I did it and didn't annotate it, I don't remember the exact model code or book I was looking at when doing the sheet.
 
@Willis,
Thanks for the info. Where can I get more information regarding the various failure modes?

I am having a hard time picturing the shear buckling failure. I presume that this is out-of-plane and not in-plane. Shear forces can be traveling parallel to the flute or perpendicular to the flute.

In a direction parallel to the flute, I can see the flutes acting as stiffened columns. How does shear buckling happen in a direction perpendicular to flutes?

Also, if I can figure the equations in the SDI manual for shear buckling (Eq 2.3-3), which gives me a PLF value, can I then use this value and divide by a cross-sectional area / foot and calculate an equivalent shear stress?

I need to compute this because one of the reviewers is calculating a stress value (16.1 MPa / 2.33 KSI) and then asking to provide diaphragm shear stresses (S12 in ETABS) to prove the metal deck works.