Do a search on "hairpin design" and you will find that this topic has been discussed a number of times, there are some very good discussions in the archives.
Two references that you can look for that have good discussions on this topic are:
"Metal Building Systems", by MBDA and Computerized Structural Design, 1980. This is out of print, but you might find it in a used book website.
"Metal Building Systems - Design and Specifications", 2nd Edition, by Alexander Newman, McGraw-Hill, 2004. Look at Chapter 12.
One concern I've always had it that if you use hairpins to resist the horizontal column reactions, then you need the floor slab in place! Many times the floor is not poured until the building is enclosed. This can be more of a problem in the northern snow country if you get a snow on the roof before the floor is poured (the snow load generally contributes more of the horizontal live load than the wind does - but not everywhere in the country).
Also, when using hairpins or tie-rods, you make the assumption that no one in the future cuts the floor slab out for a machine base and takes the hairpins or tie-rods with it!
I have also seen where the metal building is designed to sit atop of a wainscot wall (actually columns within the wall). Obviously, the column has to be checked for the horizontal loads above the floor too.
Just a few more things to consider and keep you awake at night!