Again, I do not completely understand the application. However, I will give a warning that the IEEE standards noted are not applicable for shielded MV cables with extruded insulation. Per IEEE 400-2001 DC should not be used as it can damage aged cable and will not detect most defects. I recommend at least a AC withstand or, better yet, a PD stress test. Let me know if you have any questions.
Kind regards,
-Ben
Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants