bumblebee52
Electrical
- May 11, 2010
- 2
thread238-219928 In megger's "A guide to Diagnostic Insulation Testing above 1kV" The paragraph before the Step Voltage Test section states that PI testing is not appropriate for oil filled transformers. I went to the AVO Megger Substation Maintenance Class which does instruct performing the Polarization Index test on oil filled transformers with the proviso that the results will be masked by the oil. In megger's "A stitch in time" in the Transformers sectin they mention that in the absence of more reliable data the minimum 1 minute 500 volt DC insulation resistance in megohms from winding to ground with other windings or windings guarded, or from winding to winding with core guarded is equal to C a constant for 20 degree C measurements times E voltage rating of winding under test divided by the square root of kVA rated capacity of winding under test where R is based on dry, acid-free, sludge-free oil, and bushings and terminal boards are in good condition. PRC mentions that for oil filling C-1.5 with guard and 0.8 w/o guard. Are these values for C taken at 20 degrees C for temperature of oil? What if temperature of oil is at 30 degrees C? Where do I find these values for C at different temperatures? Is there a table somewhere that gives this?
Additionlly, if PI test for oil filled transformers is not appropriate and oil masks results, can you megger an oil filled transformer with confidence or not? It seems this formula is highly dependent upon the condition of the fluid in the transformer being fairly pristine. What if the oil is not so pristine and what is the line of demarcation that determines oil is good, okay use the formula vs. not? Do we go by the FIST manual rating table for transformers?
Can we just PI the oil filled transformer and go with it?
How critically important is this masking effect anyway? Does it really skew the PI results that badly? We have about a 500 gallon transformer and the results are all in the G ohms with PI of 2 for the HV side and 1.67 and 1.91 for LV side for brand new.
If the masking is consistent, as long as I take the initial reads and track them over time to plot, that should be good enough maybe?
When we perform PI we usually use the same 5 steps as set forth in the online free AEMC instruments manaul for understanding insulation testing.
Additionlly, if PI test for oil filled transformers is not appropriate and oil masks results, can you megger an oil filled transformer with confidence or not? It seems this formula is highly dependent upon the condition of the fluid in the transformer being fairly pristine. What if the oil is not so pristine and what is the line of demarcation that determines oil is good, okay use the formula vs. not? Do we go by the FIST manual rating table for transformers?
Can we just PI the oil filled transformer and go with it?
How critically important is this masking effect anyway? Does it really skew the PI results that badly? We have about a 500 gallon transformer and the results are all in the G ohms with PI of 2 for the HV side and 1.67 and 1.91 for LV side for brand new.
If the masking is consistent, as long as I take the initial reads and track them over time to plot, that should be good enough maybe?
When we perform PI we usually use the same 5 steps as set forth in the online free AEMC instruments manaul for understanding insulation testing.