Hi,
We are trying to check the calibration of a MW transducer and display gauge. The meter is configured for 2 CT inputs and 3 voltage inputs. Unfortunately, the technicians test gear isn't too happy creating the wye-connected B-phase-grounded system that the transducer is expecting to see.
Does anyone have any bright and simple ideas for testing this? I'm thinking of either insulating the meter case and connecting B-phase to the meter ground terminal (a nuisance, as some of the transducers are awkward to remove), or attempting to scrounge 3 small isolating transformers (we are in a remote area, so may not be able to find any).
Thanks.
We are trying to check the calibration of a MW transducer and display gauge. The meter is configured for 2 CT inputs and 3 voltage inputs. Unfortunately, the technicians test gear isn't too happy creating the wye-connected B-phase-grounded system that the transducer is expecting to see.
Does anyone have any bright and simple ideas for testing this? I'm thinking of either insulating the meter case and connecting B-phase to the meter ground terminal (a nuisance, as some of the transducers are awkward to remove), or attempting to scrounge 3 small isolating transformers (we are in a remote area, so may not be able to find any).