Good morning,
Just trying to confirm what I believe to be the truth, but getting other 'eyes' on the problem never hurts.
We have a couple of buildings under construction at a high school here in southern California. Contractor ripped up an on-site 4160V feeder with his backhoe. Well we are investigating the damage and will get it fixed, however the routing of the on-site, customer owned feeders was not as the "as-built" drawings indicated. Big surprise there. Luckily no one was injured. There is a problem with the system coordination as neither the feeder breaker, nor the main system breaker cleared the fault before some SCE faciities on the service pole were damaged. But that is not the issue I am asking about here.
Anyway, the routing is such that now it will be below the slab of the new classroom building. The District asked if code required them to re-route the conduit outside the building footprint. We stated that since the feeder bypasses the building and was sufficiently deep to clear the footings, there was no code (NEC/CEC), that would require that. Just wanted to know if anyone out there has any code references that would NOT allow such an installation. I know that this is not the ideal situation, but I don't believe it is a code issue.
If anyone has information to the contrary, please enlighten me.
Thank you and regards,
EEJaime
Just trying to confirm what I believe to be the truth, but getting other 'eyes' on the problem never hurts.
We have a couple of buildings under construction at a high school here in southern California. Contractor ripped up an on-site 4160V feeder with his backhoe. Well we are investigating the damage and will get it fixed, however the routing of the on-site, customer owned feeders was not as the "as-built" drawings indicated. Big surprise there. Luckily no one was injured. There is a problem with the system coordination as neither the feeder breaker, nor the main system breaker cleared the fault before some SCE faciities on the service pole were damaged. But that is not the issue I am asking about here.
Anyway, the routing is such that now it will be below the slab of the new classroom building. The District asked if code required them to re-route the conduit outside the building footprint. We stated that since the feeder bypasses the building and was sufficiently deep to clear the footings, there was no code (NEC/CEC), that would require that. Just wanted to know if anyone out there has any code references that would NOT allow such an installation. I know that this is not the ideal situation, but I don't believe it is a code issue.
If anyone has information to the contrary, please enlighten me.
Thank you and regards,
EEJaime