Hello. I am trying to size the primary fuse for 3.75mva-33kv/480v transformer. The NEC allows primary only protection at 250% for supervised installations which is my situation. My FLA is 65amps. When looking into fuse vendor data (ie., S&C, cutler hammer, little fuse, etc...) many list a tables calling out the fuse size based on transformer KVA and primary KV. For my application the E-rated fuse typically listed is an 80E or 100E. The E-Rated fuses, be definition, trips between 200% & 240% of the E-rating in 5minutes but the curves never show at what time the fuse blows at the E-rating. This means for the 80E the fuse will blow in 5minutes between 160 & 192 amps which is out side of the required NEC 250% requirement. For a 100E blows at 200 & 240amps. I would think specifying the E rated fuse the rated should be close to the FLA? Can anyone provide any insight as to what I am misinterpreting. Thank-you very much for your time and knowledge.