Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Measuring / calculating flow-rate

Status
Not open for further replies.

45deg

Mechanical
Joined
Jul 22, 2009
Messages
1
Location
US
If I wanted to calculate the tonnage of a chiller's evaporator using the formula:

Tons = Delta_T x GPM / 24

How would I measure or calculate the GPM through the evaporator? I've been told to get it from the sales order for the chiller, but this would only give me what it is designed for and not the actual flow-rate.
 
Then, you need to go measure something, no? Presumably, something that measures velocity?

TTFN

FAQ731-376
 
There are a numbed of ways to measure water flow. Most accurate method would be to install a magnetic flow meter in the pipework but if the installation is existing options include:

- Strap-on ultrasonic flow meter
- Measure pressure loss through evaporator and compare to design pressure loss
- Pressure loss through balancing valve
- Measure pump head and extrapolate from pump curve

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top