Hello,
We are currently using a venturi for measuring our blower volume into our 2 Roasters. The average volume is 700 NM3/min. The differential of the transmitter is only 5.5" W.C. Periodically we have another group come in and, using a pitot tube, take samples and calculate the volume. We seem to be finding that the venturi reading vs. the pitot samples are differing by a greater amount. I would like to know if any one out there has had better success with an anubar or flowbar rather than a venturi for measuring a blower volume.
Thanks
We are currently using a venturi for measuring our blower volume into our 2 Roasters. The average volume is 700 NM3/min. The differential of the transmitter is only 5.5" W.C. Periodically we have another group come in and, using a pitot tube, take samples and calculate the volume. We seem to be finding that the venturi reading vs. the pitot samples are differing by a greater amount. I would like to know if any one out there has had better success with an anubar or flowbar rather than a venturi for measuring a blower volume.
Thanks