Apr 1, 2011 #1 salem Electrical Joined May 2, 2001 Messages 38 Location AE how to measure (test) the zero sequence impedance of two winding, three phase Dyn11 33/11 kV 15 MVA transformer?
how to measure (test) the zero sequence impedance of two winding, three phase Dyn11 33/11 kV 15 MVA transformer?
Apr 1, 2011 #2 davidbeach Electrical Joined Mar 13, 2003 Messages 9,551 Location US See thread238-295543. Upvote 0 Downvote
Apr 6, 2011 Thread starter #3 salem Electrical Joined May 2, 2001 Messages 38 Location AE For a Dyn transformer, is the following correct: - 3 phase at delta side to be shorted together. - 3 phase at y side to be shorted together. - apply the voltage between one of the phases at y side and nutral. - Z0 will be equall to V/I Upvote 0 Downvote
For a Dyn transformer, is the following correct: - 3 phase at delta side to be shorted together. - 3 phase at y side to be shorted together. - apply the voltage between one of the phases at y side and nutral. - Z0 will be equall to V/I
Apr 6, 2011 #4 davidbeach Electrical Joined Mar 13, 2003 Messages 9,551 Location US Apply the voltage that produces full rated current. The per cent of rated voltage is the per cent impedance. Upvote 0 Downvote
Apply the voltage that produces full rated current. The per cent of rated voltage is the per cent impedance.