measurement of transformer zero sequence impedance

Status
Not open for further replies.

salem

Electrical
May 2, 2001
38
how to measure (test) the zero sequence impedance of two winding, three phase Dyn11 33/11 kV 15 MVA transformer?
 
Replies continue below

Recommended for you

For a Dyn transformer, is the following correct:

- 3 phase at delta side to be shorted together.
- 3 phase at y side to be shorted together.
- apply the voltage between one of the phases at y side and nutral.
- Z0 will be equall to V/I
 
Apply the voltage that produces full rated current. The per cent of rated voltage is the per cent impedance.
 