measure sequence
ftova
CO
hi everybody
i need help about how measure Positive, Negative y Zero sequence voltages and currents
url`s, pdf`s or comments are wellcomed
thanks in advance
Fredrick
Do a search on symmetrical components. Most protective relay manufacturers have info on their sites, like SEL and Basler.
Zero Sequence: With a window CT the three in wye-connected system would have a current in it equal to 3Ia0. Also if each phase current is known, the average values (including the phase angul) will be equate to the zero sequence
Positive Sequence: Is the average value of adding the phase current A plus the current on phase B shifted 1200 plus adding the C phase current shifted -1200 will be equivalent to the positive sequence current.
Negative Sequence: Is the average value of adding the phase current A plus the current on phase B shifted -1200 plus adding the C phase current shifted 1200 will be equivalent to the negative sequence current.
Similar approach can be used for the voltage.
There are a few ways of measuring 3I0 or measuring 3V0. Other than that, what's measured is nearly always phase quantities and the sequence quantities are calculated rather than measured. Almost anything I work with these days the residual current (3I0) is always calculated unless it's the 3I0 in the neutral of a transformer. I can't think of any new installations where we'd attempt to measure 3V0.