There are a few ways of measuring 3I0 or measuring 3V0. Other than that, what's measured is nearly always phase quantities and the sequence quantities are calculated rather than measured. Almost anything I work with these days the residual current (3I0) is always calculated unless it's the 3I0 in the neutral of a transformer. I can't think of any new installations where we'd attempt to measure 3V0.