Hi all,
IEEE standard voltages specifies 69kV system nominal wherein the maximum voltage is specified at 72.5 kV.
However, our application calls for 72kV L-L system nominal voltage. This 72 kV powerline is fed from a 260-72kV Wye-wye (solidly grounded primary and 150A resistor grounded secondary)100MVA power transformer. The transformer has OLTC on the primary with AVR set to maintain 72kV nominal at its secondary.
The lightning arresters installed at the 72kV lines (fed from 150A resistor grounded system) are ABB EXLIM R with MCOV rating of 67kV which I believe is under-rated. For resistance grounded systems, the phase-ground voltages of the unfaulted phases may rise up to line-line (72kV) as the neutral will shift on a bolted line-ground fault. If this happens, the LAs will fail or "conduct" currents to ground resulting to a 3LG fault.
We did not perform any EMTP study on the lines nor calculated the COG of the 72kV system but I believe the conservative theory should be sound enough.
One consultant disagrees with me saying that the ground fault will not be maintained and will be cleared immediately by the protection system within 0.5 seconds. However, I still have concern that the LA would fail. Can anyone help me get some light considering that our nominal system voltage is not standard as published in IEEE Std C62.22-2009.
IEEE standard voltages specifies 69kV system nominal wherein the maximum voltage is specified at 72.5 kV.
However, our application calls for 72kV L-L system nominal voltage. This 72 kV powerline is fed from a 260-72kV Wye-wye (solidly grounded primary and 150A resistor grounded secondary)100MVA power transformer. The transformer has OLTC on the primary with AVR set to maintain 72kV nominal at its secondary.
The lightning arresters installed at the 72kV lines (fed from 150A resistor grounded system) are ABB EXLIM R with MCOV rating of 67kV which I believe is under-rated. For resistance grounded systems, the phase-ground voltages of the unfaulted phases may rise up to line-line (72kV) as the neutral will shift on a bolted line-ground fault. If this happens, the LAs will fail or "conduct" currents to ground resulting to a 3LG fault.
We did not perform any EMTP study on the lines nor calculated the COG of the 72kV system but I believe the conservative theory should be sound enough.
One consultant disagrees with me saying that the ground fault will not be maintained and will be cleared immediately by the protection system within 0.5 seconds. However, I still have concern that the LA would fail. Can anyone help me get some light considering that our nominal system voltage is not standard as published in IEEE Std C62.22-2009.