Dear Mr. NickParker (Electrical)(OP)10 Jan 23 13:20
"....Why MCCB+Contactor is used for Non-Motor circuits? "
I am fully in agreement with learned advice by Mr. xnuke
I only wish to submit the following for general information purposes:
1. MCCBs are NOT mechanically designed for:
(a) high frequency of ( i.e. on-off-on ) switching within a short time continuously,
(b) high number of electrical and mechanical operations.
1.1. Contactors are design for high frequency and numbers of electrical and mechanical operations.
2. In this MCCB in series with Contactor arrangement, for higher reliability reasons; the combination should be Type 2 co-ordination . See IEC for detail. In brief, the MCCB shall trip for any short-circuit but the Contactor shall NOT be damaged but should be inspected which is allowed (to break open the lightly-welded contacts), if any.
3. Note: The terminology Type 2 coordination is used in IEC world. It is unknow/not used in the US, ANSI, UL, NEMA, NEC....
Che Kuan Yau (Singapore)