JensenDrive
Electrical
- May 25, 2007
- 120
I noticed recently that Eaton sent in some submittals for 480V MCCs with bus where they say ampacity is based on 105C max operating temperature in a 40C ambient. Then they connect circuit breakers directly to the bus, and the circuit breakers have terminal temperatures limited to 75C. The also install CTs around the bus with a thermal rating factor of 1.0 at 30C. I find the highest temp you can get a CT rated for is 55C. I challenged the matter, and Eaton only stated that this was OK per UL standard 845. I have found that Eaton uses this same 105C bus rating in 480V switchgear and panelboards. Do all MCC/electrical panel mfrs use this same high bus temp with equipment rated much less than 105C? Does this concern anyone?