Apr 14, 2019 #1 jrrocks Mechanical Joined Aug 13, 2018 Messages 58 Location IN Hi, In Distribution board, I seen kA (SC) rating of 415V 3P 32A MCB as 25kA which is more than designed for the panel (as compare to panel SLD 10kA) What could be the consequences for selecting higher kA MCB?
Hi, In Distribution board, I seen kA (SC) rating of 415V 3P 32A MCB as 25kA which is more than designed for the panel (as compare to panel SLD 10kA) What could be the consequences for selecting higher kA MCB?
Apr 14, 2019 #2 RRaghunath Electrical Joined Aug 19, 2002 Messages 1,741 Location IN Nothing really. 25kA rating in place of 10kA rated MCB is no problem. If it happens to be other way round, it will have dire consequences. Upvote 0 Downvote
Nothing really. 25kA rating in place of 10kA rated MCB is no problem. If it happens to be other way round, it will have dire consequences.
Apr 15, 2019 Thread starter #3 jrrocks Mechanical Joined Aug 13, 2018 Messages 58 Location IN Thank you..!!! Upvote 0 Downvote